On Wed, 21 Oct 2009, Arjen de Korte wrote:
Citeren Justin Piszcz <[email protected]>:
Even without the poll option, the error persists, but it takes longer to
trigger (3-5 minutes vs. 1-2 minutes @ 5 second follreq)
Have you also tried setting
pollinterval = 10
in ups.conf, to increase the polling interval for this UPS?
If this doesn't work either, I fear there is little else we can do for you.
Occasionally, the connection may be lost (due to EMI, plugging other devices
on the same USB bus, etc), but if this happens almost every minute, there
must be something wrong.
The connection to the UPS should be fairly reliable, if not this is either
kernel or hardware related. It doesn't seem to be the first, so your only
other option would be to try this on different hardware (which would be a
nice test, to see if you don't just happen to have a broken USB controller on
your mainboard).
Best regards, Arjen
--
Please keep list traffic on the list
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
Hi,
If there was a problem with the USB bus, would attached CD/DVD & keyboard
and mouse devices / usb sticks also have problems?
I only have problems with the UPS.
I power cycled the UPS and reconnected it, and the problem persists.
Could this be a newly discovered issue with the latest USB chips in the
Intel P55 chipset?
Justin.
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser