Citeren Michelle Wright <michelle.wri...@gmail.com>:

$ upsc upsname
battery.charge.low: 38
battery.charge.warning: 38
battery.type: PbAc
device.mfr: Emerson Network Power
device.model: LiebertPSP
device.serial:
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.vendorid: 10af
driver.version: 2.4.3
driver.version.data: Belkin HID 0.12
driver.version.internal: 0.34
ups.mfr: Emerson Network Power
ups.model: LiebertPSP
ups.productid: 0001
ups.serial:
ups.status: OB

OB = On Battery

ups.vendorid: 10af

/etc/nut/ups.conf
[upsname]
        driver = usbhid-ups
        port = auto
        vendorid = 10af

Remove the 'vendorid' line. It isn't needed.

        desc = "Server UPS"

In /var/log/daemon and also the cgi web interface it thinks it is
running on battery though!

That's what 'ups.status' is telling too, so I'm not surprised about that. Are you absolutely sure you plugged the device in a live outlet? If you are, running

    /path/to/usbhid-ups -DDD -a upsname

might give us something to work with. Make sure you stop all drivers before running this.

Best regards, Arjen
--
Please keep list traffic on the list