Citeren David Varley <[email protected]>:

I've just set up a CyberPower Value 2200E-GP on a system running Lucid
AMD64, with the current NUT package via apt-get, and it seems to be working
fine for me with the usbhid-ups driver, so I guess it can go in the HCL?

Probably. We'll just need a little more information like the 'upsc' output for this UPS (to see if we need to add additional mappings).

I'm using the system to host several virtual servers under KVM, and to make
things simple I set it up to hibernate rather than shutdown, that way all
the guest OS don't have to be shutdown, they just carry on happily from
where they were after power is restored. To achieve this I timed how long it
take to go into hibernation (30-40 seconds), and set the UPS to shutdown
after 60 seconds via the driver "offdelay" setting.
I then set:

    SHUTDOWNCMD "/sbin/upsdrvctl shutdown;/usr/sbin/pm-hibernate"

and under test it works well. I'm don't know if there is a better or "right"
way to do this, obviously the heuristically determined off delay is a bit of
a risk, and as the system doesn't actually shut down perhaps there will be
other problems with NUT? The /etc/killpower flag isn't deleted, for
instance.

Remember that the 'upsd' server will latch the FSD (forced shutdown) flag when it has detected an "OB LB" condition. The only way to reset this, is to restart NUT. Otherwise after resuming, NUT will immediately shutdown again. Many systems will allow you to run scripts when going into hibernation and after resuming. You'll want to stop NUT when hibernating and restart it when resuming (this will take care of the /etc/killpower flag as well). I'd prefer to run the 'upsdrvctl shutdown' command from the hibernation script as well. Also remember that there is a slight risk that if hibernation fails, the UPS will power off anyway. If that worries you, it might be better to stick with a full shutdown of the system.

I've attached the output of  *usbhid-ups -DDD -a 2200LCD* as there seem to
be several errors reported in there. I can see the subdriver doesn't find
the serial number, for example, while the pwrstat code supplied by
CyberPower does.

There are some issues with the usbhid-ups driver in nut-2.4.3. Most of these have been resolved in the development version of NUT. I would be grateful if you could try out this. Most (if not all) of the errors you're seeing now should be fixed.

We could add some code to add reading the serial number, but we really need it before claiming the device (which seems to be broken in either your UPS or the version of libusb you're using).

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to