Arjen de Korte <nut+users <at> de-korte.org> writes:

> 
> Citeren Kevin <bakdong <at> gmail.com>:
> 
> >    0.686325     Initiating UPS shutdown
> >    0.686340     upsdrv_shutdown...
> >    0.686365     instcmd(shutdown.return, [NULL])
> >    0.686382     find_nut_info: unknown info type: shutdown.return
> 
> This is normal. Some UPS'es (models that have a HID layer around an  
> essential serial interface) support a command that will result in what  
> NUT calls 'shutdown.return', so that's what we try first. A true HID  
> PDC UPS (like the APC models you have) don't, so this command is not  
> found. This is exactly what we expect.
> 
> >    0.686398     instcmd(load.on.delay, 30)
> >    0.686433     Unit = 00001001, UnitExp = 0
> >    0.686450     Exponent = 0
> >    0.686464     PhyMax = 0, PhyMin = 0, LogMax = 32767, LogMin = -1
> >    0.690437     Report[set]: (3 bytes) => 28 1e 00
> >    0.690437     Set report succeeded
> >    0.690437     instcmd: SUCCEED
> 
> In a HID PDC UPS, you need to set both the timer for shutdown and  
> (re)start independently. They start counting down immediately after  
> setting the report, so we set the (re)start timer...
> 
> >    0.690437     instcmd(load.off.delay, 20)
> >    0.690437     Unit = 00001001, UnitExp = 0
> >    0.690437     Exponent = 0
> >    0.690437     PhyMax = 0, PhyMin = 0, LogMax = 32767, LogMin = -1
> >    0.695437     Report[set]: (3 bytes) => 12 14 00
> >    0.695437     Set report succeeded
> >    0.695437     instcmd: SUCCEED
> 
> ...before the stop timer, so that we don't get stuck if the power is  
> lost. In that case, the (re)start timer will have expired and a UPS  
> will not start again.
> 
> > APC CS 500
> > This shuts down the APC CS 500 after 20 seconds.  (and it stays shutdown)
> 
> This probably means the driver called 'load.off.delay 20', which is  
> the last resort option for the usbhid-ups. It looks like it doesn't  
> have a mapping for 'shutdown.reboot', which the logs you have produced  
> should reveal.
> 
> > APC Smart-UPS 1000
> > If the power is left on, switches to battery and back online after 2 
seconds.
> 
> Either the HID PDC implementation in this UPS is broken or what you're  
> seeing is 'shutdown.reboot'. The timers are in seconds and with mains  
> present, the UPS should stop 20 seconds after running this command and  
> resume again 10 (30-20) seconds later.
> 
> > If the power is off, goes to sleep after 90 seconds. (and comes back  
> > on when the power is connected)
> 
> This is broken either way. There is nothing we can do about that.
> 
> Best regards, Arjen

Thanks for the response. 

I have to say that this is way beyond me. We know that the UPS models in 
question support the function that we want (sleep/hibernate), and we know the 
command that is needed to initiate that state. It's been working in previous 
releases on at least the Smart-UPS 1000, and it was working with a small 
amendment to the code on the old hidups module.

It's a shame that I can't seem to get the up to date releases working properly 
on both of these UPS models, specially after seeing that it can be done, 
apparently fairly simply, by sending the 0xff86007c code in both cases.

Anyway, at lease I have now shared the very limited knowledge that I have 
gained 
from the exercise with the NUT user community, so maybe, hopefully, someone 
will 
be able to benefit from it in the future.

Regards,
Kevin.



_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to