on 23/01/2011 16:16 Arjen de Korte wrote:
Citeren Kevin <[email protected]>:

I see my error now. The above line should be moved up to before the first occurence of { "ups.delay.shutdown", ... }. The first available HID path that is found, will set the NUT mapping and there is one before this line now, so the above will never be used in its present location.

Ok, try again....

{ "ups.delay.start", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.PowerSummary.DelayBeforeStartup", NULL, DEFAULT_ONDELAY, HU_FLAG_ABSENT, NULL}, { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.APCShutdownAfterDelay", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL }, { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.PowerSummary.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, HU_FLAG_ABSENT, NULL}, { "ups.timer.start", 0, 0, "UPS.PowerSummary.DelayBeforeStartup", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL}, { "ups.timer.shutdown", 0, 0, "UPS.PowerSummary.DelayBeforeShutdown", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL}, { "ups.timer.reboot", 0, 0, "UPS.PowerSummary.DelayBeforeReboot", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
  /* used by APC SmartUPS RM */
{ "ups.delay.start", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.DelayBeforeStartup", NULL, DEFAULT_ONDELAY, HU_FLAG_ABSENT, NULL}, { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, "UPS.Output.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, HU_FLAG_ABSENT, NULL}, { "ups.timer.start", 0, 0, "UPS.Output.DelayBeforeStartup", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL}, { "ups.timer.shutdown", 0, 0, "UPS.Output.DelayBeforeShutdown", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL}, { "ups.timer.reboot", 0, 0, "UPS.Output.DelayBeforeReboot", NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},


Different....

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 90
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d


./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 231.8
output.voltage: 231.8
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d


Sorry....

# ./clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 231.8
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: 88
ups.timer.start: 248
ups.vendorid: 051d


delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:88 START:248
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:88 START:248
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:86 START:246
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:86 START:246

Regards,
Kevin.

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to