Citeren Kevin <[email protected]>:

Different....

# ./clients/upsc apc1500

[...]

ups.delay.shutdown: 90
ups.delay.start: 250

This is what I expected to happen. The value of ups.delay.shutdown is now read from the UPS...

./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
OK

# ./clients/upsc apc1500

[...]

ups.delay.shutdown: 30
ups.delay.start: 250

..and apparently can be written as well.

Sadly, it looks like this value is used for a different purpose than setting the minimum delay value before shutdown (like I expected). Unless you're willing to dig deeper into this, I think we have to conclude that this model doesn't allow setting the delay values lower than 90 seconds. Using an 'ondelay' value of 100, does the UPS cycle the output if mains is present? And does it wait until the mains return if it is not present?

I would still like to see the full output of the below command. An earlier version you posted was incomplete (the report descriptor was missing, which is vital to be able to check our HID parser without access to a specific UPS model). Could you please post the output of

   /path/to/usbhid-ups -DD -a apc1500 > APC_Smart-UPS_1000.log 2>&1

here? The redirection of stderr to stdin was probably missing in your previous post.

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to