Thanks for clearing that out, I was going to do a battery test because I was
afraid that my batteries might be dying but as it turns out one of the
batteries had a loose plug, fixed that and the ups is running strong :)


>Only if the UPS finds that the battery needs to be replaced it will report
the 'RB' status (replace battery). If it doesn't, all is well. The Q1
>protocol that is used by your UPS doesn't support more verbose messages
(and neither does it report runtime or charge capacity) so there is >nothing
more to report.

When using the software supplied from the manufacturer I do see runtime and
charge capacity messages.

Best regards
-Gardar

On Fri, Mar 11, 2011 at 7:28 AM, Arjen de Korte <[email protected]>wrote:

> Citeren Garðar Arnarsson <[email protected]>:
>
>  Thanks a bunch, that worked like a charm :)
>>
>
> Glad to hear that.
>
>
>  But now I've got another question... After I run commands (tests) with
>> upscmd, where do I see the results?
>>
>
> You don't.
>
>
>  Ran a battery test check and it did not give any output.
>>
>
> Only if the UPS finds that the battery needs to be replaced it will report
> the 'RB' status (replace battery). If it doesn't, all is well. The Q1
> protocol that is used by your UPS doesn't support more verbose messages (and
> neither does it report runtime or charge capacity) so there is nothing more
> to report.
>
>
> Best regards, Arjen
> --
> Please keep list traffic on the list (off-list replies will be rejected)
>
>
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
>



-- 
Garðar Arnarsson
kerfisstjóri Giraffi sf.
[email protected]
http://gardar.giraffi.net
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to