On Thursday 11 August 2011 10.55.39 Gémes Géza wrote: > Hi, Hi Géza.
> I've got an AEC Star T4110 connected with an RS232 port by a megatec cable. > On the list of supported devices > (http://www.networkupstools.org/stable-hcl.html) there is only one AEC > device, so I tried genericups with upstype=21. The problem is, that the > UPS (while being on-line) reports constantly being on battery. > # upsc aec ups.status > OB The only thing I could found on AEC T4(110), that it is a RS232 and have 'dry contact' and 'SNMP' as option. And as it is a online ups and at least 10KVA, I think it has some intelligent communication. So I don't think it is a working on the generic driver. If you don't have the 'dry contact' option installed. > My question is: > What is the recommended procedure to debug this (what parameters try to > change in what order)? > About the system: > Ubuntu 10.04 (kernel 2.6.32-33-generic) > NUT: 2.4.3-1ubuntu3.1 > I think it talks some megatec protocol. So if you can upgrade to a new NUT and test the 'blazer_ser' driver. Or the megatec driver in 2.4. Run it in debug mode. Locate where you have the ups driver. Then do /path/to/megatec -DD -a myups Where myups is the tag in the ups.conf [myups] driver=megatec port= /dev/ttyS0 (end by CTRL+c) Cheers /Kjell _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser