Hi Kjell,
> On Thursday 11 August 2011 10.55.39 Gémes Géza wrote:
>> Hi,
> Hi Géza.
>
>> I've got an AEC Star T4110 connected with an RS232 port by a megatec cable.
>> On the list of supported devices
>> (http://www.networkupstools.org/stable-hcl.html) there is only one AEC
>> device, so I tried genericups with upstype=21. The problem is, that the
>> UPS (while being on-line) reports constantly being on battery.
>> # upsc aec ups.status
>> OB
> The only thing I could found on AEC T4(110), that it is a RS232 and have
> 'dry contact' and 'SNMP' as option. And as it is a online ups and at least
> 10KVA, I think it has some intelligent communication.
>
> So I don't think it is a working on the generic driver. If you don't have the
> 'dry contact' option installed.
>
>> My question is:
>> What is the recommended procedure to debug this (what parameters try to
>> change in what order)?
>> About the system:
>> Ubuntu 10.04 (kernel 2.6.32-33-generic)
>> NUT: 2.4.3-1ubuntu3.1
>>
> I think it talks some megatec protocol. So if you can upgrade to a new NUT
> and test the 'blazer_ser' driver. Or the megatec driver in 2.4.
>
> Run it in debug mode. Locate where you have the ups driver. Then do
>
> /path/to/megatec -DD -a myups
>
> Where myups is the tag in the ups.conf
>
> [myups]
> driver=megatec
> port= /dev/ttyS0
>
>
> (end by CTRL+c)
>
> Cheers
> /Kjell
Thank you for your help.
Unfortunately it isn't working.
I have nut version 2.4.3-1ubuntu3.1 , so have tried the megatec driver:
[aec]
driver=megatec
port= /dev/ttyS0
The output of # /lib/nut/megatec -DDDDDDDDDDDDDD -a aec
is:
Network UPS Tools - Megatec protocol driver 1.6 (2.4.3)
0.000000 send_to_all: SETINFO driver.parameter.port "/dev/ttyS0"
0.000111 debug level is '14'
0.001356 DTR=1, RTS=0
0.001404 send_to_all: SETINFO device.type "ups"
0.001424 send_to_all: SETINFO driver.version "2.4.3"
0.001450 send_to_all: SETINFO driver.version.internal "1.6"
0.001470 send_to_all: SETINFO driver.name "megatec"
0.001485 Starting UPS detection process...
0.001505 Asking for UPS information [I]...
2.503689 I => FAILED [timeout]
2.503712 Asking for UPS status [Q1]...
5.105909 Q1 => FAILED [timeout]
5.105930 Asking for UPS status [Q1]...
7.708115 Q1 => FAILED [timeout]
7.708134 Asking for UPS status [Q1]...
10.310381 Q1 => FAILED [timeout]
10.310404 Megatec protocol UPS not detected.
So it seams that it isn't "speaking" any megatec dialect :-(
Cheers
Geza