On Sep 30, 2011, at 10:23 AM, Arnaud Quette wrote:

Hi Simon,

2011/8/30 Dwyer, Simon <[email protected]>:
Hi All,

I have got the Belkin F6S600auUSB UPS working with the blazer_usb driver.

I pulled the power to the ups last night and it sent a message to the server saying it was on battery then ran for another 10 minutes and then sent a message to the server telling it to shut down, which it did.

upswr did not return anything.

[root@verity ~]# upsc ups
battery.voltage: 13.50
battery.voltage.nominal: 12.0
beeper.status: enabled
device.type: ups
driver.name: blazer_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.internal: 0.03
input.current.nominal: 2.0
input.frequency: 49.9
input.frequency.nominal: 50
input.voltage: 242.9
input.voltage.fault: 242.9
input.voltage.nominal: 230
output.voltage: 237.5
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 0
ups.productid: 5161

Arnaud - this     ^^^^

ups.status: OL
ups.temperature: 25.0
ups.type: offline / line interactive
ups.vendorid: 0665

and this?        ^^^^



[root@verity ~]# upscmd -l ups
Instant commands supported on UPS [ups]:

beeper.toggle - Toggle the UPS beeper
load.off - Turn off the load immediately
load.on - Turn on the load immediately
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start - Start a battery test
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test

If any more info is needed just let me know.

thanks for your report.
I've just committed this entry in the trunk, r3264.
for the sake of completion, could you also tell us what are the USB
VendorID and ProductID?

cheers,
Arnaud


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to