Am 30.09.2011 16:23, schrieb Arnaud Quette:
Hi Simon,

2011/8/30 Dwyer, Simon<[email protected]>:
Hi All,

I have got the Belkin F6S600auUSB UPS working with the blazer_usb driver.

I pulled the power to the ups last night and it sent a message to the server 
saying it was on battery then ran for another 10 minutes and then sent a 
message to the server telling it to shut down, which it did.

upswr did not return anything.

[root@verity ~]# upsc ups
battery.voltage: 13.50
battery.voltage.nominal: 12.0
beeper.status: enabled
device.type: ups
driver.name: blazer_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.internal: 0.03
input.current.nominal: 2.0
input.frequency: 49.9
input.frequency.nominal: 50
input.voltage: 242.9
input.voltage.fault: 242.9
input.voltage.nominal: 230
output.voltage: 237.5
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 0
ups.productid: 5161
ups.status: OL
ups.temperature: 25.0
ups.type: offline / line interactive
ups.vendorid: 0665


[root@verity ~]# upscmd -l ups
Instant commands supported on UPS [ups]:

beeper.toggle - Toggle the UPS beeper
load.off - Turn off the load immediately
load.on - Turn on the load immediately
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start - Start a battery test
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test

If any more info is needed just let me know.

thanks for your report.
I've just committed this entry in the trunk, r3264.
for the sake of completion, could you also tell us what are the USB
VendorID and ProductID?

cheers,
Arnaud

Stated above, same for the FSP EP-1K, except of temperature and battery voltage:

battery.charge: 100
battery.runtime: 4000
battery.voltage: 27.40
battery.voltage.nominal: 24.0
beeper.status: enabled
device.type: ups
driver.flag.novendor: enabled
driver.name: blazer_usb
driver.parameter.chargetime: 8
driver.parameter.idleload: 30
driver.parameter.pollinterval: 15
driver.parameter.port: auto
driver.parameter.productid: 5161
driver.parameter.runtimecal: 1200,100,3200,50
driver.parameter.vendorid: 0665
driver.version: 2.4.3
driver.version.internal: 0.03
input.current.nominal: 5.0
input.frequency: 50.1
input.frequency.nominal: 50
input.voltage: 231.2
input.voltage.fault: 231.2
input.voltage.nominal: 220
output.voltage: 231.2
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 27
ups.productid: 5161
ups.status: OL
ups.type: offline / line interactive

Cmds an Alarms untested but the EP-650 is already in the supported devices list.

Can You confirm no usb req timeouts for Your device at 2sec polling for hours?

Oct  1 06:24:28 fritz.box blazer_usb[11636]: Communications with UPS lost: 
status read failed!
Oct  1 06:24:43 fritz.box blazer_usb[11636]: Communications with UPS lost: 
status read failed!
Oct  1 06:24:58 fritz.box blazer_usb[11636]: Communications with UPS 
re-established

USB-Sniffing the proprietary viewpower software I found it uses another protocol, with 
"QPI" requests 1/sec,
sniff dumps attached (propably off list due to size limits).

I will try some replays with a modified blazer_usb driver or dummy-ups and 
tools/device-recorder.sh.

y
tom


Attachment: viewpower-fsp-ep-1k-usbsniff.tar.bz2
Description: application/bzip