On 09/08/2012, at 23:37, Arnaud Quette <[email protected]> wrote:
> sorry for the time taken to provide you an answer, but there it is :)

No problem, I am happy you could try it on the same hardware .

> There is a data (HID: UPS.PowerSummary.PresentStatus.Switchable) that wasn't 
> mapped in NUT.
> This data allows to send shutdown order to the UPS, and is equivalent to what 
> you have on the LCD screen of the UPS.
> 
> I've not seen this before because this data is enabled by default...

Hmm, what parameter is it called on the LCD panel?

I was on holiday when the UPS was tested and shipped so I didn't get a chance 
to try things myself.

> The fix is both attached (limited to the code) and committed to the trunk 
> r3717:
> http://trac.networkupstools.org/projects/nut/changeset/3717
> 
> Once applied, check with upsc that "ups.shutdown" is set to "enabled".
> Otherwise, use:
> # upsrw -u <user> -p <password> -s ups.shutdown="enabled" <device name>
> 
> You can then test it using "upsmon -c fsd" if you have protected loads, or 
> simply with:
> # upscmd -u <user> -p <password>  <device name> shutdown.return
> 
> Can you please confirm back that the issue is closed on your side?

I should be able to try it later on today, or tomorrow.

Thanks again!

--
Daniel O'Connor software and network engineer
for Genesis Software - http://www.gsoft.com.au
"The nice thing about standards is that there
are so many of them to choose from."
  -- Andrew Tanenbaum
GPG Fingerprint - 5596 B766 97C0 0E94 4347 295E E593 DC20 7B3F CE8C






Attachment: smime.p7s
Description: S/MIME cryptographic signature

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to