Hi Dan,

2012/8/10 Daniel O'Connor <[email protected]>

>
> On 09/08/2012, at 23:37, Arnaud Quette <[email protected]> wrote:
> > sorry for the time taken to provide you an answer, but there it is :)
>
> No problem, I am happy you could try it on the same hardware .
>

sure, it's always better to ensure a user problem is solved.


> > There is a data (HID: UPS.PowerSummary.PresentStatus.Switchable) that
> wasn't mapped in NUT.
> > This data allows to send shutdown order to the UPS, and is equivalent to
> what you have on the LCD screen of the UPS.
> >
> > I've not seen this before because this data is enabled by default...
>
> Hmm, what parameter is it called on the LCD panel?
>

Refer to the manual:
http://pqtools.eaton.com/download/intl/products/comet-ex-rt/148-man_uk_08.pdf
page 27, chapter 3, ON/OFF features => UPS ON/OFF by software

the parameter I've added in NUT (ups.shutdown) is directly connected to the
same data than the above LCD feature.

I was on holiday when the UPS was tested and shipped so I didn't get a
> chance to try things myself.
>

the danger of letting other do the work ;-)


> > The fix is both attached (limited to the code) and committed to the
> trunk r3717:
> > http://trac.networkupstools.org/projects/nut/changeset/3717
> >
> > Once applied, check with upsc that "ups.shutdown" is set to "enabled".
> > Otherwise, use:
> > # upsrw -u <user> -p <password> -s ups.shutdown="enabled" <device name>
> >
> > You can then test it using "upsmon -c fsd" if you have protected loads,
> or simply with:
> > # upscmd -u <user> -p <password>  <device name> shutdown.return
> >
> > Can you please confirm back that the issue is closed on your side?
>
> I should be able to try it later on today, or tomorrow.
>
> Thanks again!
>

ok, let me know if you still face any issue.
I'll be on vacation at the end of next week...

cheers,
Arnaud
-- 
Linux / Unix / Opensource Engineering Expert - Eaton -
http://opensource.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to