quick question, Is there an issue with centos 5 that prevents it from
running Nut greater then 2.2.3 ?
On 09/25/2012 07:02 PM, Charles Lepple wrote:
On Sep 25, 2012, at 4:31 PM, [email protected] wrote:
Hey all,
I have a triplite 1050 and when I did a test today I saw that the battery
bounce from 100 to 80 to 90 to 91 percent before UPSD lost its connection to
the UPS. The server then decided that it was time to shut off.
The UPS sat at 91% for about 5 min before UPSD lost its connection, so I'm not
sure if it wasn't updating its battery.charge... I wasn't sure if this is
expected behavior...
If upsd loses its connection to the driver, and the last status was "on
battery", it assumes the worst, and attempts to shut down.
Luckily this was a planned test and my script just outputs to messages that it
believes it is time to shut off.
upsc ups
battery.charge: 91
battery.test.status: Battery OK
battery.voltage: 13.00
battery.voltage.nominal: 18
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.2.2
driver.version.internal: 0.11.1
input.voltage: 0.00
input.voltage.nominal: 120
output.voltage: 118.0
ups.debug.load_banks: 0
ups.debug.V: 31 30 33 30 58 58 0d '1030XX.'
ups.delay.shutdown: 64
ups.firmware: F0957.B
ups.firmware.aux: protocol 2001
ups.mfr: Tripp Lite
ups.model: OMNISMART1050
ups.power.nominal: 1050
ups.status: OB
Sep 25 15:34:43 server kernel: hiddev96: USB HID v1.00 Device [TRIPP LITE TRIPP
LITE OMNISMART1050 ] on usb-0000:00:1f.2-2
Broadcast message from nut (Tue Sep 25 15:34:44 2012):
Communications with UPS [email protected] lost
Sep 25 15:34:44 server upsmon[18224]: Poll UPS [[email protected]] failed - Driver
not connected
Sep 25 15:34:44 server upsmon[18224]: Communications with UPS [email protected] lost
Sep 25 15:34:44 server wall[3925]: wall: user nut broadcasted 1 lines (44 chars)
Sep 25 15:34:49 server upsmon[18224]: Poll UPS [[email protected]] failed - Driver
not connected
It looks like the kernel rediscovered the UPS at 15:34:43. How much time had
elapsed since you cut power?
This version of NUT (2.2.2) is fairly old - newer versions of the USB code in
NUT will attempt to reconnect more aggressively. I don't remember if this
particular version is prone to crashing when an UPS disconnects, but that might
have been the impetus behind some of the changes since then.
Also, is the UPS plugged directly into the server with a short USB cable? UPS
tests and power failures can cause USB interference. A hub should theoretically
work, but it is probably not something to rely on.