I took the log. Here's what happened.
Broadcast Message from nut@rasp
        (somewhere) at 16:18 ...
UPS BNT500AP@localhost battery needs to be replaced

occurred when for the first time value "1" was read as 
"UPS.PowerSummary.PresentStatus.NeedReplacement", on this line:
6409.240690     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x0a, Offset: 6, Size: 1, Value: 1
It happened for 9 times, but the message appeared only on first.

Broadcast Message from nut@rasp
        (somewhere) at 17:33 ...

UPS BNT500AP@localhost on battery
occurred when UPS.PowerSummary.PresentStatus.ACPresent turned to 0 on this line:
10921.069403    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0

Broadcast Message from nut@rasp
        (somewhere) at 17:33 ...

UPS BNT500AP@localhost on line power

There were 3 more "on battery" events at 2:31:
43194.030619    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
Here I also see a suspisious frequency value 70. How is this possible?
43194.046966    Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
Offset: 0, Size: 8, Value: 70

At 2:58:
44790.984549    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
Here all voltages and frequencies are OK, so I don't understand why ACPresent 
is 0.
44790.374516    Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, Offset: 
0, Size: 16, Value: 232
44790.375512    Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
Offset: 0, Size: 8, Value: 50
44790.376535    Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, 
Offset: 0, Size: 16, Value: 232
44790.377511    Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, 
Offset: 0, Size: 8, Value: 50

and at 6:15:
56597.541128    Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0

At 6:15 I also got "Low battery" event that triggered Raspberry pi shutdown, 
but I don't see a reason for that in the driver log.
When it happened, the UPS started beeping every 2 seconds and I could silence 
it by pressing the power button, as written in user manual. I was only able to 
silence it by shutting down completely. By the way, the first time it happened 
also at about the same time.
I'm not able to post the log, because even compressed it is more than 1 MB.

-----Original Message-----
From: Charles Lepple [mailto:[email protected]] 
Sent: Saturday, June 08, 2013 10:49 PM
To: Mārtiņš Puķītis
Cc: 'nut-upsuser lists.alioth.debian.org'
Subject: Re: [Nut-upsuser] several problems with Powercom BNT-500AP

On Jun 8, 2013, at 12:57 PM, Mārtiņš Puķītis wrote:

> I'll take a longer driver log. This page 
> (http://www.networkupstools.org/support.html) says that to take a driver log 
> NUT should be stopped, so I won't be able to tell when these events occurred 
> within a driver log.

Hmm, I didn't realize it said that, but I think that's to prevent having two 
copies of the same driver running at the same time. (That's even more difficult 
to decipher from one log alone.)

You can either just restart the driver, or restart upsd after stopping 
everything.

In either case, I was thinking that it would be useful to know where *in the 
longer log* the events occur. Then we can look to see if the UPS is returning 
bad information, or if the driver is experiencing an error condition.

-- 
Charles Lepple