Hello.

It's been a while since I started this topic. I've finally tested it on Linux 
desktop PC.
Nut version 2.6.4-2.3
Basically the behavior is the same as on raspberry pi. It reports "battery 
needs to be replaced" regularly and I got "on battery" message

114107.780504   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
(on line nr. 1044540 in log)

after ~ 31 hours of testing along with immediate "low battery (critical)"

not sure, but probably because of
114107.780620   Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x0a, Offset: 4, Size: 1, Value: 1
(on line nr. 1044544 in log)

message.
Full zipped log (5,8 MB) with -DDD driver debug level available at
http://wikisend.com/download/396966/upsdebug.zip
As before, no power failure was present at the time this happened. The UPS at 
the time I bought it (in June) was capable of supplying backup power for PC for 
more than 15 minutes.

Martins Pukitis.


-----Original Message-----
From: Charles Lepple [mailto:[email protected]] 
Sent: Tuesday, June 11, 2013 4:27 PM
To: Mārtiņš Puķītis
Cc: nut-upsuser lists.alioth.debian.org; [email protected]
Subject: Re: [Nut-upsuser] several problems with Powercom BNT-500AP

[I am CC'ing Alexey from Powercom in case he has seen any of these issues with 
the Raspberry Pi hardware.]

On Jun 10, 2013, at 1:05 PM, Mārtiņš Puķītis wrote:

> I took the log. Here's what happened.
> Broadcast Message from nut@rasp
>        (somewhere) at 16:18 ...
> UPS BNT500AP@localhost battery needs to be replaced
> 
> occurred when for the first time value "1" was read as 
> "UPS.PowerSummary.PresentStatus.NeedReplacement", on this line:
> 6409.240690   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
> Input, ReportID: 0x0a, Offset: 6, Size: 1, Value: 1
> It happened for 9 times, but the message appeared only on first.

Correct, upsmon throttles the REPLBATT event:

http://www.networkupstools.org/docs/man/upsmon.conf.html (search for RBWARNTIME)

> Broadcast Message from nut@rasp
>        (somewhere) at 17:33 ...
> 
> UPS BNT500AP@localhost on battery
> occurred when UPS.PowerSummary.PresentStatus.ACPresent turned to 0 on this 
> line:
> 10921.069403  Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
> ReportID: 0x0a, Offset: 2, Size: 1, Value: 0

If you turn up the debugging level from 2 to 3, the driver will do a hex dump 
of the report buffer. Offset and size are bits, so if the ACPresent bit is 0, 
that's what the driver reports.

> Here I also see a suspisious frequency value 70. How is this possible?
> 43194.046966  Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
> Offset: 0, Size: 8, Value: 70

Similar situation to ACPresent - if those are the bits coming in, that's what 
the driver reports. Granted, there are cases where usbhid-ups might be 
misinterpreting those bits, but as you can imagine, it is hard to test all of 
the corner cases. We should be getting an error message from usbhid-ups if the 
USB reply is not long enough.

> At 2:58:
> 44790.984549  Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
> ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
> Here all voltages and frequencies are OK, so I don't understand why ACPresent 
> is 0.

usbhid-ups does not look at voltage and frequency to determine whether AC is 
present. Voltage and frequency values can be averages over time (with the 
averaging being performed in the UPS microprocessor), so the driver simply 
trusts the ACPresent bit returned by the UPS.

I'm starting to wonder if the USB controller or driver in the Raspberry Pi is 
flaky. We have seen odd issues with other ARM/Linux boards, and none of the 
symptoms are the same as on x86 PCs.

Do you have a desktop or laptop Linux system where you can test this?

-- 