Matt Ivie wrote, On 7/31/2013 8:14 AM:
On Wed, 2013-07-17 at 23:33 -0400, Charles Lepple wrote:
On Jul 17, 2013, at 11:27 AM, Matt Ivie wrote:
I'm really just looking for a UPS that might run a couple of small
servers and other small devices(routers or switches).
Good call on including the network gear in the power budget. NUT isn't much use
to the slave systems if the network connection between master and slave goes
down.
If I could get
15-30 minutes of runtime from the batts and o course run the automated
shutdown and reboot sequence through nut that would be great. The server
I'm looking at has a PSU capable of 200W but I don't expect to be maxing
out the system capabilities at all. I'll be running either Debian
Wheezy(most likely) or Trisquel 6.0 and I'd like to just use the
pre-packaged version of NUT rather than building a new package if I can.
It doesn't look like I can just copy-and-paste the link to the exact result,
but if you go to the UPS selector on the Eaton Power Quality page, they will
recommend a few models:
http://powerquality.eaton.com/
The NUT HCL spells out Powerware 9130/9140, but the Eaton pages refer to PW9130
and PW9140. Pretty sure they are the same unit with a different name.
Debian wheezy has NUT 2.6.4, which should cover most of the units that Eaton's
selector would recommend.
You could also go with a Tripplite rack-mount UPS, but a lot of the low-end
ones use a proprietary protocol that seems to change between model years.
What about the Eaton 5S series? Does it go under a different name on the
compatibility list or is it just not compatible?
It's standard USB HID, so that's a good sign that it will work fine. The
5S must not have been out long, they were lacking a good
desktop/workstation computer line-interactive unit, this one looks nice.
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser