On 08/10/2013 11:43 PM, Roger Price wrote:
OpenSUSE 12.3 has fully embraced systemd, but to get NUT working
correctly now requires some further systemd engineering in addition to
the usual NUT configuration files.  A new systemd service unit is needed
to power off the UPS.

The service unit consists of a new file
/etc/systemd/system/ups-delayed-shutdown.service

    [Unit]
    Description=Initiate delayed UPS shutdown
    Before=umount.target
    DefaultDependencies=no

    [Service]
    Type=oneshot
    ExecStart=/usr/lib/ups/driver/upsdrvctl shutdown

    [Install]
    WantedBy=poweroff.target

This service unit should be enabled with root command

    systemctl --system reenable
/etc/systemd/system/ups-delayed-shutdown.service

I have tested this setup with 64 bit openSUSE 12.3 and NUT 2.6.5 using
an Eaton Ellipse ASR 1500 USBS.  9 seconds after server poweroff, the
UPS powers off.  When wall power returns the server restarts correctly.

What exactly is this supposed to do?

When system is shutting down because of power failure (and low battery)
ups should be powered off with
/lib/systemd/system-shutdown/nutshutdown
script. That's also the correct location for ups shutdown script. It's executed after everything else. Using Before=umount.target is especially bad bad idea. It's not guaranteed that umount sync can finish in time, so you can have power down during filesystem sync with all the consequences.

Michal

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser