On 19/09/13 01:30, Kris Jordan wrote:
> Luke-Jr wrote, On 9/18/2013 1:02 PM:
>> I wanted to suggest some rating for functionality. I got the UPS
>> available
>> that seemed to have the best possible rating from NUT's list (Eaton
>> Powerware
>> UPS 1500), and found out it doesn't support telling me battery level or
>> runtime! :/
> 
> I'm avoiding Eaton/Powerware because the lack of usbhid support, the
> bcmxcp driver doesn't report much

bootc@tarquin ~ $ upsc pw9120
ambient.temperature: 10
ambient.temperature.high: 40
battery.charge: 100
battery.runtime: 720
battery.voltage:  26.0
device.mfr: Eaton
device.model: PW9120 700i
device.serial: RY346A0036
device.type: ups
driver.name: bcmxcp_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.shutdown_delay: 60
driver.version: 2.6.5
driver.version.internal: 0.26
input.frequency: 50.0
input.frequency.high: 52
input.frequency.low: 48
input.frequency.nominal: 50
input.transfer.boost.high: 184
input.transfer.high: 276
input.transfer.low: 160
input.transfer.trim.low: 264
input.voltage: 245
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 0
outlet.2.id: 2
outlet.2.status: On
output.current:  2.1
output.current.nominal:  3.0
output.frequency: 50.0
output.phases: 1
output.voltage: 231
output.voltage.nominal: 230
ups.beeper.status: disabled
ups.firmware: Cont:02.60 Inve:02.60
ups.load:  65.6
ups.mfr: Eaton
ups.model: PW9120 700i
ups.power: 459
ups.power.nominal: 700
ups.serial: RY346A0036
ups.status: OL
ups.test.result: Done and passed

It doesn't?

> but I have heard that someone is
> working on it.

Eaton actually employs the NUT project lead, Arnaud Quette, so yes it's
safe to say someone is working on NUT and the bcmxcp driver.

With that said, the Eaton logo is now conspicuously absent from the NUT
home page. Eaton is still mentioned on
http://www.networkupstools.org/acknowledgements.html and NUT is
mentioned on http://powerquality.eaton.com/opensource/Default.asp

HTH,
Chris

-- 
Chris Boot
[email protected]

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to