Charles Lepple wrote, On 9/19/2013 7:49 PM:
On Sep 19, 2013, at 12:11 PM, Paul O'Rorke wrote:

So where does this leave things regards Eaton and shut down?  Has anyone 
managed graceful shut down from an Eaton unit with either of the ushhid or 
bcmxcp drivers?
Generally speaking, the UPS will signal when it reaches a low battery state, regardless of whether 
the UPS publishes runtime statistics, battery percentages, or any other such values. The real 
difference between a "smart" and "dumb" UPS is not just the protocol, but how 
advanced the battery monitoring and charging circuitry is.

I have an old MGE UPS that uses the usbhid-ups driver, and I have no problems shutting 
down the system via the LB signal in NUT. The non-Powerware-based Eaton units can be 
considered "descendants" of this hardware, from what I understand, and provide 
similar variables.

I was able to change battery.charge.low to 50 (*) on an Evolution 850. I tested that the setting took, even if the UPS was rebooted. Because it's powering Win2k3, I changed the offdelay to 600 and the ondelay to 615. I then disabled the beeper. It all works, so I'm pretty happy with the driver capability with this UPS. Driver: usbhid-ups.

(*) You don't have to neccessarily use a timeout script to keep from draining the battery.


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to