On 20/12/13 21:22, Charles Lepple wrote:
>
> Maybe Dan, the maintainer of the nutdrv_qx driver, has better insight on 
> this, but my uneducated guess is that I don't think it is Megatec/Qx. The 
> logs don't show any commands going down to the UPS, just Interrupt Read 
> requests to EP1IN.
>
> It definitely won't be covered by stock usbhid-ups either, although it does 
> implement the bare minimum of the USB HID protocol. (The usbhid-ups driver 
> expects USB HID PDC.)

I did try both blazer_usb and usb hid, neither one worked.
>
> What might be interesting is whether any of the bits vary when the UPS goes 
> on battery, or when the battery gets low. You may want to plug in a dummy 
> load, and power the computer from another UPS or the wall outlet, in order to 
> fully characterize the protocol.
Ok, I did this, here is how it went (approximately):
t=0     power on the UPS, with some load.
t=2 min unplug the UPS from mains, alarm goes off.
t=33 min low battery alarm goes off.
t=35 min ups powers down.

As I was doing the test, I added load, to speed up the battery drain,
but  from the dumps I don't thing that's reported. The win software
tells very little about the status of the UPS.

This time, I added another capture point, a software running inside the
vm (usbsniff), in case for some reason commands sent to the ups where
missing.
Here are the results (the list would hold large messages):
http://www.ariwainer.com.ar/varios/ups/2013-12-21-usbmon-fullcycle.log
http://www.ariwainer.com.ar/varios/ups/2013-12-21-usbsniff-fullcycle.log
http://www.ariwainer.com.ar/varios/ups/2013-12-21-wireshark-fullcycle.pcapng
> Also important are the settings in the UPS monitoring software, such as 
> timeouts, or behavior options for when the power returns. Those will probably 
> show up as magic numbers later on.
>

I have this:
Shutdown delay on AC fail: 15 minutes.
Shutdown delay on low battery: 1 minute.
Warning message interval: 15 seconds.

Let me know if further tests or more info are needed.

Kind regards.

Ari.