On Jan 1, 2014, at 1:52 PM, Ariel Wainer wrote:

> Very strange! It seems like the completly powered down and OK status
> yeild the same reading. The reading didn't change after plugging back in
> the AC.

Well, as strange as that is, I don't think it would be a common case. 
Ordinarily, the load would be the computer monitoring the UPS, and if the load 
is off... We can certainly document that, though.

In your testing, do you have suggestions on better debug levels? We should 
probably log the status changes at level 2 or less, since the hex dump is only 
useful for those who know the protocol. Also, I'm not sure how many of the 
messages we should print while scanning the bus.

Good to hear that the rest of the driver works. Can you check the shutdown 
feature? (run the driver with "-k", or execute "upsdrvctl shutdown"). I wonder 
if the "0x01" in the shutdown command corresponds to the time between when the 
command is sent, and when the UPS actually turns off the load.

-- 
Charles Lepple
clepple@gmail