On Jan 10, 2014, at 4:46 PM, Ariel Wainer wrote: > On 10/01/14 01:53, Charles Lepple wrote: >> I am curious about why the Interrupt Out packet is sent by the Windows >> software if it isn't to turn off the UPS. Is it possible to do some more >> testing with shorter timeouts so that the battery doesn't get depleted? You >> would need to record the exact time when it shuts down, I think. > > Sure, I will do the test during the weekend.
If it's not too late for your tests, I committed a v0.03 to the 'atcl' branch, with string matching to avoid confusion with other 0001:0000 devices. > I'm not sure if it's related, but, using the driver these days I noted > that I sometimes the connection to the ups drops and resets, like this, > while I hear the click sound of a relay: We've definitely heard of cases where an UPS will generate enough noise on the USB bus that it disconnects. The best we can do is try to re-attach to the same device when it comes back. The current driver should handle this - if not, please send debug output from the driver. (Probably at least -DDD) -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser