On Jan 10, 2014, at 4:46 PM, Ariel Wainer wrote:

> On 10/01/14 01:53, Charles Lepple wrote:
>> I am curious about why the Interrupt Out packet is sent by the Windows 
>> software if it isn't to turn off the UPS. Is it possible to do some more 
>> testing with shorter timeouts so that the battery doesn't get depleted? You 
>> would need to record the exact time when it shuts down, I think.
> 
> Sure, I will do the test during the weekend.

If it's not too late for your tests, I committed a v0.03 to the 'atcl' branch, 
with string matching to avoid confusion with other 0001:0000 devices.

> I'm not sure if it's related, but, using the driver these days I noted
> that I sometimes the connection to the ups drops and resets, like this,
> while I hear the click sound of a relay:

We've definitely heard of cases where an UPS will generate enough noise on the 
USB bus that it disconnects. The best we can do is try to re-attach to the same 
device when it comes back. The current driver should handle this - if not, 
please send debug output from the driver. (Probably at least -DDD)

-- 
Charles Lepple
clepple@gmail




_______________________________________________