On Jan 21, 2014, at 8:05 AM, Rafał Oleszek wrote:

> MONITOR UPS_251@localhost 2 monmaster password master
> MONITOR UPS_252@localhost 2 monmaster password master

I think the "2"s here should be "1".

"powervalue is an integer representing the number of power supplies that the 
UPS feeds *on this system*."

So if UPS_251 is connected to one power supply on the system running upsmon, 
and UPS_252 is connected to another, then each powervalue is 1.

> MINSUPPLIES 2

Or you could change this to 4, but that masks what is actually going on.

-- 
Charles Lepple