I tried all options: 1,2 and in MINSUPPLIES: 1,2,3,4 still didn't work. UPS_251 and UPS_252 feeds all environment and it's not feed directly one server, but many of them.
> On Jan 21, 2014, at 8:05 AM, Rafał Oleszek wrote: > >> MONITOR UPS_251@localhost 2 monmaster password master >> MONITOR UPS_252@localhost 2 monmaster password master > > I think the "2"s here should be "1". > > "powervalue is an integer representing the number of power supplies that > the UPS feeds *on this system*." > > So if UPS_251 is connected to one power supply on the system running > upsmon, and UPS_252 is connected to another, then each powervalue is 1. > >> MINSUPPLIES 2 > > Or you could change this to 4, but that masks what is actually going on. > > -- > Charles Lepple > clepple@gmail > > > > > _______________________________________________ > Nut-upsuser mailing list > [email protected] > http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser