On Dec 1, 2014, at 4:11 AM, Victor Porton <por...@narod.ru> wrote:

> battery.voltage: 13.70
> battery.voltage.high: 13.00
> battery.voltage.low: 10.40

These are the voltage thresholds for the UPS, so theoretically the UPS will 
send the LB signal when the battery voltage goes lower than 10.40 Volts.

Also, if battery.charge works, you can use "ignorelb" if you want to shut down 
at another level of charge:

http://www.networkupstools.org/docs/man/ups.conf.html#_ups_fields

> ups.delay.shutdown: 30
> ups.delay.start: 180

These timers are in seconds. You will want to verify this, but according to 
those values, the UPS will shut off its output 30 seconds after the shutdown 
signal (so you need to make sure that your OS shutdown takes less time than 
that).

Does "upsrw -l advice" show anything?

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to