01.12.2014, 14:50, "Charles Lepple" <[email protected]>:
> On Dec 1, 2014, at 4:11 AM, Victor Porton <[email protected]> wrote:
>> battery.voltage: 13.70
>> battery.voltage.high: 13.00
>> battery.voltage.low: 10.40
>
> These are the voltage thresholds for the UPS, so theoretically the UPS will
> send the LB signal when the battery voltage goes lower than 10.40 Volts.
>
> Also, if battery.charge works, you can use "ignorelb" if you want to shut
> down at another level of charge:
>
> http://www.networkupstools.org/docs/man/ups.conf.html#_ups_fields
>> ups.delay.shutdown: 30
>> ups.delay.start: 180
>
> These timers are in seconds. You will want to verify this, but according to
> those values, the UPS will shut off its output 30 seconds after the shutdown
> signal (so you need to make sure that your OS shutdown takes less time than
> that).
>
> Does "upsrw -l advice" show anything?
$ upsrw -l advice
upsrw: invalid option -- 'l'
Network UPS Tools upsrw 2.7.2
usage: upsrw [-h]
upsrw [-s <variable>] [-u <username>] [-p <password>] <ups>
Demo program to set variables within UPS hardware.
-h display this help text
-s <variable> specify variable to be changed
use -s VAR=VALUE to avoid prompting for value
-u <username> set username for command authentication
-p <password> set password for command authentication
<ups> UPS identifier - <upsname>[@<hostname>[:<port>]]
Call without -s to show all possible read/write variables.
--