On Dec 11, 2014, at 12:31 PM, [email protected] wrote: > This is the output with line power turned off. ... > 0.361090 Report[get]: (2 bytes) => 03 0d > 0.361210 Path: 008c0001.008c0004, Type: Input, ReportID: 0x03, Offset: 0, > Size: 8, Value: 13 > 0.361246 Report[buf]: (2 bytes) => 03 0d > 0.361274 Path: 008c0001.008c0004, Type: Feature, ReportID: 0x03, Offset: > 0, Size: 8, Value: 13 > This is a starting point: compare with line power on, where the value was 0x0c (12).
> -------------------------------------------------------------------- > This is a diferent output with line on and the following commad line ... > 0.347847 Report[get]: (2 bytes) => 03 0d > 0.347926 Path: 008c0001.008c0004, Type: Input, ReportID: 0x03, Offset: 0, > Size: 8, Value: 13 > 0.347965 Report[buf]: (2 bytes) => 03 0d > 0.347994 Path: 008c0001.008c0004, Type: Feature, ReportID: 0x03, Offset: > 0, Size: 8, Value: 13 Are you sure that this was with the line power on? I have no idea why it is the same value for 008c0004 as with line power off. (Ignore the "string_to_path" lines, they are looking for values for a different type of Liebert/Phoenixtec UPS, and they did not find anything.) -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser