On Mar 13, 2015, at 10:53 AM, Philip Taylor <[email protected]> wrote:

> I’ve set up UPSMON to simply execute ‘shutdown -h now’ and my system shuts 
> down when I type ‘upsmon -c fsd’. The problem is that the OpenUPS doesn’t 
> shut down as a result; and therefore when the power comes back on, unless the 
> battery has totally run out, the system stays dead. Once the battery dies 
> completely, the UPS will reboot itself and turn the server on - but this may 
> never happen.
> 
> Do I have to modify the Centos ’shutdown’ script to add to it ‘upsdrvctl 
> shutdown’ at it’s end point? Or should the fact that upsd is run as a service 
> (nut-server.service on Centos 7) do this without my intervention?

Again, I don't know what CentOS does with its shutdown scripts. Other 
distributions have some sort of hook that calls 'upsdrvctl shutdown' near the 
end of the shutdown process.

> I’ve looked at ‘ignorelb’. As far as I can tell the OpenUPS never sends LB; 
> which may be a calibration issue; but there is no documentation to tell you 
> how this should work. Their documentation talks about ‘coulomb counters’ and 
> ‘fuel gauges’ but says nothing about how it’s implemented! And I’m waiting 
> for a response from their support desk.
> 
> You say 'NUT takes a conservative approach to USB HID drivers’. I get a few 
> errors and I don’t know if they matter. Like :

What I meant is that usbhid-ups doesn't try to interpret all of the HID items, 
just the ones that are known to contain good values (for some version of the 
UPS firmware).

> when I plug in the OpenUPS I see this : 
> 
> [   49.049586] usb 4-5: new full-speed USB device number 3 using ohci-pci
> [   49.215825] usb 4-5: New USB device found, idVendor=04d8, idProduct=d004
> [   49.222717] usb 4-5: New USB device strings: Mfr=1, Product=2, 
> SerialNumber=4
> [   49.229879] usb 4-5: Product: OPEN-UPS
> [   49.233658] usb 4-5: Manufacturer: Mini-Box.Com
> [   49.238218] usb 4-5: SerialNumber: PBSO4-LiFePO
> [   49.259143] hid-generic 0003:04D8:D004.0002: invalid report_size 248
> [   49.265603] hid-generic 0003:04D8:D004.0002: item 0 1 1 7 parsing failed
> [   49.272485] hid-generic: probe of 0003:04D8:D004.0002 failed with error -22

You can ignore the hid-generic errors; NUT detaches that kernel driver and 
bypasses it with libusb.

That said, it means the HID descriptor has some syntax issues.

> If I manually run 'upsdrvctl start’ I get this :
> 
> USB communication driver 0.32
> Using subdriver: openUPS HID 0.4
> libusb_get_string: Invalid argument
> libusb_get_string: Invalid argument

The driver should only call libusb_get_string() for informational purposes, so 
it should only affect ups.mfr and ups.model in upsc.

> 
> And if I run upsd with high level of debug, after working OK for a while, I 
> see these ‘broken pipe’ messages :
> 
>    0.419974   Entering libusb_get_report
>    0.421967   Report[get]: (4 bytes) => 60 c4 ff 3b
>    0.422056   PhyMax = 0, PhyMin = 0, LogMax = 16777215, LogMin = 0
>    0.422069   Unit = 00001001, UnitExp = 0
>    0.422080   Exponent = 0
>    0.422093   hid_lookup_path: 00840004 -> UPS
>    0.422107   hid_lookup_path: 00840024 -> PowerSummary
>    0.422121   hid_lookup_path: 00850068 -> RunTimeToEmpty
>    0.422146   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 
> 0x60, Offset: 0, Size: 24, Value: 3.9321e+06

That looks like a calibration problem: 3.9 million seconds of runtime is a 
while.

>    0.422163   Report[buf]: (4 bytes) => 60 c4 ff 3b
>    0.422177   PhyMax = 0, PhyMin = 0, LogMax = 16777215, LogMin = 0
>    0.422188   Unit = 00001001, UnitExp = 0
>    0.422198   Exponent = 0
>    0.422209   hid_lookup_path: 00840004 -> UPS
>    0.422221   hid_lookup_path: 00840024 -> PowerSummary
>    0.422234   hid_lookup_path: 00850068 -> RunTimeToEmpty
>    0.422253   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x
> 60, Offset: 0, Size: 24, Value: 3.9321e+06
>    0.422264   Entering libusb_get_report
>    0.423983   Can't retrieve Report b1: Broken pipe
>    0.424034   hid_lookup_path: ff000001 -> not found in lookup table
>    0.424060   hid_lookup_path: ff000001 -> not found in lookup table
>    0.424076   Path: ff000001.ff000001, Type: Output, ReportID: 0xb1, Offset: 0
> , Size: 248
>    0.424089   Entering libusb_get_report
>    0.425933   Can't retrieve Report b2: Broken pipe
>    0.425953   hid_lookup_path: ff000001 -> not found in lookup table
>    0.425966   hid_lookup_path: ff000001 -> not found in lookup table
>    0.425980   Path: ff000001.ff000001, Type: Input, ReportID: 0xb2, Offset: 0,
>  Size: 248
>    0.425992   Entering libusb_get_report
>    0.427956   Can't retrieve Report 81: Broken pipe
>    0.428006   hid_lookup_path: ff000001 -> not found in lookup table
>    0.428021   hid_lookup_path: ff000001 -> not found in lookup table
>    0.428036   Path: ff000001.ff000001, Type: Output, ReportID: 0x81, Offset: 0
> , Size: 248
>    0.428048   Entering libusb_get_report
>    0.429891   Can't retrieve Report 82: Broken pipe
>    0.429911   hid_lookup_path: ff000001 -> not found in lookup table
>    0.429925   hid_lookup_path: ff000001 -> not found in lookup table
>    0.429939   Path: ff000001.ff000001, Type: Input, ReportID: 0x82, Offset: 0,
>  Size: 248
>    0.429950   Entering libusb_get_report

Can you send a copy of the debug output (-DDD) from starting the driver for ~30 
seconds, gzip'd and attached?

-- 
Charles Lepple