I here is some information I could have provided previously.  Here is what I am 
seeing:

====================================================================

Broadcast message from [email protected] (Fri May 13 22:31:35 2016):

UPS myups@localhost on battery
upsc myups@localhost
battery.charge: 3
battery.charge.low: 10
battery.charge.warning: 30
battery.runtime: 93
battery.temperature: 32.9
battery.type: PbAC
battery.voltage: 46.4
battery.voltage.nominal: 48.0
device.mfr: Tripp Lite
device.model: TRIPP LITE SMART2200RM2UN
device.serial: nunyabiznis
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.5
driver.version.data: TrippLite HID 0.8
driver.version.internal: 0.37
input.frequency: 0.0
input.transfer.high: 0.0
input.transfer.low: 0.0
input.transfer.reason: input voltage out of range
input.voltage: 0.0
input.voltage.nominal: 120
output.current: 2.00
output.frequency: 60.0
output.frequency.nominal: 60
output.voltage: 0.0
output.voltage.nominal: 120
ups.beeper.status: muted
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 17
ups.mfr: Tripp Lite
ups.model: TRIPP LITE SMART2200RM2UN
ups.power: 0.0
ups.power.nominal: 2200
ups.productid: 3015
ups.serial: 2608CY0SM882500034
ups.status: OB DISCHRG
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 09ae
ups.watchdog.status: 0

[root@localhost Downloads]# upsc myups@localhost ups.status
OB DISCHRG

[root@localhost Downloads]#
Broadcast message from [email protected] (Fri May 13 22:34:35 2016):

UPS myups@localhost on line power

upsc myups@localhost ups.status
OL CHRG
====================================================================


It won't provide a "LB" status.


Thanks again for the help.

--
Kamran Khan
PSSC Labs
HPC Software / Technical Engineer
________________________________
From: Nut-upsuser 
<[email protected]> on behalf of 
Kamran Khan <[email protected]>
Sent: Friday, May 13, 2016 3:30:00 PM
To: [email protected]
Subject: [Nut-upsuser] Low Battery event not occurring


Hi Everyone,


New to the list.  Thanks in advance for any assistance you are able to provide.


I have a TrippLite SMART2200RM2UN UPS.  I have installed and configured NUT as 
instructed on the website, and am able to monitor the status of the UPS without 
much problem.  The only problem I am seeing is that I cannot get the machine to 
actually send a Low Battery ( LB ) signal.


When I run "upsc myups@localhost", the "battery.charge.low" is "10".  My 
current "battery.charge" is "6".  However, when I type "upsc myups@localhost 
ups.status", it only shows OB and DISCHRG, not LB.


If I understand the NUT process correctly, it looks for this LB status in order 
to create the POWERDOWNFLAG.  "In upsmon.conf, add a POWERDOWNFLAG directive 
with a filename. upsmon will create this file when the UPS needs to be powered 
off during a power failure when low battery is reached."


Please let me know if you need me to provide any further information.  Again, 
any help is greatly appreciated.


Thanks.

--
Kamran Khan