> > battery.charge: 3 > battery.charge.low: 10 > battery.charge.warning: 30 > battery.runtime: 93 > battery.temperature: 32.9 > battery.type: PbAC > battery.voltage: 46.4 > battery.voltage.nominal: 48.0
Is it possible that battery.charge is really 30% rather than 3%? The 3016 protocol models have issues with scaling on some of the voltages and frequencies. You can see this by killing the driver, and restarting it with '-DDD'. If you want to mail that log to the list, please gzip it first. Also, only about the first minute would be necessary. > device.mfr: Tripp Lite > device.model: TRIPP LITE SMART2200RM2UN > device.serial: nunyabiznis Pretty sure the letters in the serial numbers are uppercase :-) Given how many of the model names are reused for very different hardware, it can be helpful to see at least the first few digits of a serial number, but in this case, I don't think we have too many other reports of this hardware to go on. The closest ones seem to be: http://networkupstools.org/ddl/Tripp_Lite/SMART2200RMXL2U.html > If I understand the NUT process correctly, it looks for this LB status in > order to create the POWERDOWNFLAG. "In upsmon.conf, add a POWERDOWNFLAG > directive with a filename. upsmon will create this file when the UPS needs to > be powered off during a power failure when low battery is reached." That is correct. You can also configure NUT drivers to ignore the UPS's LB flag and synthesize it from battery.charge or battery.runtime: http://networkupstools.org/docs/man/ups.conf.html (search for 'ignorelb') -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser