[please use reply-all when responding - the list does not mangle reply-to 
headers. thanks!]

On Jun 22, 2016, at 4:06 AM, André Hänsel wrote:
> 
> On Mittwoch, 22. Juni 2016 09:21 André wrote:
> 
>> Hi list,
>> 
>> (I think) I understand that in upsmon.conf, the MONITOR line ends with
>> "master" or "slave". Basically if it's master it will wait for slaves to
>> shut down and if it's slave it will signal the master to switch off the UPS
>> after shutdown.

if it is a slave, it *allows* the master to switch off the UPS. I am not 
familiar with the exact sequence of events if there is no master upsmon process.

https://github.com/networkupstools/nut/blob/master/clients/upsmon.c#L615

>> 
>> To be able to monitor a network UPS as a slave, there must be a user in
>> upsd.users on the master system. This user needs to have a setting named
>> "upsmon" set.
>> 
>> And this is where I'm confused - this setting has a parameter that must
>> also be set to either " master" or "slave". What do I set this to?
>> 
>> Regards,
>> André
> 
> Ok, I did some further testing and it seems that setting "upsmon slave" does
> not allow clients to connect, so when would I want to set it?
> 

The "upsmon slave" setting should not prevent clients from connecting. Can you 
provide more details about the system? If this is a distributor-provided 
package, did they link against TCP-wrappers (using /etc/hosts.deny)?

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to