Hi

debian jessie, nut 2.7.2-4

APC Smart-UPS 1500 connected through USB, running nut driver usbhid-ups


This UPS powers my switches, internet connection and my monitor server that monitors this and my other UPSes + runs smokeping and nagios.


But recently a powerloss seemed to have shutdown my monitor PC immediately, so it did not shut down the other servers cleanly. Power seem to be lost immediately.


But my APC Smart-UPS 1500 always reported everything OK.

output from CGI scripts

APC Smart-UPS 1500 - powers switches and routers in little rack +++ also this server dkfitlet Smart-UPS 1500 ONLINE
        100 %   227.5   227.5   20.8 %  39.6 °C         00:17:00        All data

UPS Model:      Smart-UPS 1500
Status:         ONLINE
Runtime:        00:17:00
Battery:        27.1 V
Input:  226.0 V
Output:         226.0 V
        0.94 A
        50.0 Hz


when I go into treemode though, I see something interesting


APC Smart-UPS 1500 - powers switches and routers in little rack +++ also this server dkfitlet
battery.charge  :       100
battery.charge.low      :       10
battery.charge.warning  :       50
battery.mfr.date        :       2005/08/26
battery.runtime         :       1020
battery.runtime.low     :       120
battery.temperature     :       39.6
battery.type    :       PbAc
battery.voltage         :       27.1
battery.voltage.nominal         :       24.0
device.mfr      :       American Power Conversion
device.model    :       Smart-UPS 1500
device.serial   :       AS0535132782
device.type     :       ups
driver.name     :       usbhid-ups
driver.parameter.pollfreq       :       30
driver.parameter.pollinterval   :       2
driver.parameter.port   :       auto
driver.parameter.serial         :       AS0535132782
driver.version  :       2.7.2
driver.version.data     :       APC HID 0.95
driver.version.internal         :       0.38
input.sensitivity       :       high
input.transfer.high     :       253
input.transfer.low      :       208
input.voltage   :       226.0
output.current  :       0.94
output.frequency        :       50.0
output.voltage  :       226.0
output.voltage.nominal  :       230.0
ups.alarm       :       No battery installed!
ups.beeper.status       :       enabled
ups.delay.shutdown      :       20
ups.delay.start         :       30
ups.firmware    :       653.12.I
ups.firmware.aux        :       4.2
ups.load        :       20.8
ups.mfr         :       American Power Conversion
ups.mfr.date    :       2005/08/26
ups.model       :       Smart-UPS 1500
ups.productid   :       0002
ups.serial      :       AS0535132782
ups.status      :       ALARM OL
ups.test.result         :       No test initiated
ups.timer.reboot        :       -1
ups.timer.shutdown      :       -1
ups.timer.start         :       -1
ups.vendorid    :       051d



what? no battery installed, and the status is ALARM? how come NUT doesnt report this?


root@dkfitlet:/etc/nut# upslog -s apc1500 -l -
Network UPS Tools upslog 2.7.2
logging status of apc1500 to - (30s intervals)
Init SSL without certificate database
20170403 154055 100 230.4 21.4 [ALARM OL] NA NA
20170403 154125 100 230.4 20.8 [ALARM OL] NA NA
20170403 154155 100 230.4 21.4 [ALARM OL] NA NA




root@dkfitlet:/etc/nut# upsmon -DDD
Network UPS Tools upsmon 2.7.2
kill: No such process
   0.000000     UPS: apc1500@localhost (monitoring only)
   0.000214     UPS: Smart-UPS_3000@localhost (monitoring only)
   0.000328     UPS: R3000XR@localhost (monitoring only)
   0.001278     Using power down flag file /etc/killpower
   0.002126     debug level is '3'
   0.005831     Init SSL without certificate database
   0.011754     Trying to connect to UPS [apc1500@localhost]
   0.013150     Can not connect to localhost in SSL, continue uncrypted
   0.013909     Logged into UPS apc1500@localhost
   0.014384     pollups: apc1500@localhost
   0.014501     get_var: apc1500@localhost / status
   0.014889     parse_status: [ALARM OL]
   0.015012     parsing: [ALARM]
   0.015100     parsing: [OL]
   0.015181     ups_on_line: apc1500@localhost (first time)


notice the value of parsing, first it is ALARM, and then OL. But if only the last value is returned, then everything seems okay and NUT never reports the issue?


for my other UPS'es it looks like this, only ever having OL as value.

   0.015265     Trying to connect to UPS [Smart-UPS_3000@localhost]
   0.016294     Can not connect to localhost in SSL, continue uncrypted
   0.017190     Logged into UPS Smart-UPS_3000@localhost
   0.017673     pollups: Smart-UPS_3000@localhost
   0.017779     get_var: Smart-UPS_3000@localhost / status
   0.018083     parse_status: [OL]
   0.018178     parsing: [OL]
   0.018261     ups_on_line: Smart-UPS_3000@localhost (first time)
   0.018344     Trying to connect to UPS [R3000XR@localhost]
   0.019224     Can not connect to localhost in SSL, continue uncrypted
   0.020028     Logged into UPS R3000XR@localhost
   0.020600     pollups: R3000XR@localhost
   0.020704     get_var: R3000XR@localhost / status
   0.021046     parse_status: [OL]
   0.021144     parsing: [OL]
   0.021228     ups_on_line: R3000XR@localhost (first time)




JonB