On 03/04/17 18.05, Tim Dawson wrote:
NUT can only report what the UPS tells it. IE, if no battery/load test is runs
on the UPS, it has no way to know the battery croaked . . . it just sees normal
voltage, and says "100% charge" . . . .


yeah, but the UPS does also tell NUT:

root@dkfitlet:/etc/nut# upslog -s apc1500 -l -
Network UPS Tools upslog 2.7.2
logging status of apc1500 to - (30s intervals)
Init SSL without certificate database
20170403 154055 100 230.4 21.4 [ALARM OL] NA NA
20170403 154125 100 230.4 20.8 [ALARM OL] NA NA
20170403 154155 100 230.4 21.4 [ALARM OL] NA NA


root@dkfitlet:/etc/nut# upsmon -DDD
Network UPS Tools upsmon 2.7.2
kill: No such process
   0.000000    UPS: apc1500@localhost (monitoring only)
   0.000214    UPS: Smart-UPS_3000@localhost (monitoring only)
   0.000328    UPS: R3000XR@localhost (monitoring only)
   0.001278    Using power down flag file /etc/killpower
   0.002126    debug level is '3'
   0.005831    Init SSL without certificate database
   0.011754    Trying to connect to UPS [apc1500@localhost]
   0.013150    Can not connect to localhost in SSL, continue uncrypted
   0.013909    Logged into UPS apc1500@localhost
   0.014384    pollups: apc1500@localhost
   0.014501    get_var: apc1500@localhost / status
   0.014889    parse_status: [ALARM OL]
   0.015012    parsing: [ALARM]
   0.015100    parsing: [OL]
   0.015181    ups_on_line: apc1500@localhost (first time)



however, I have to go into debug level 2 to see that.



root@dkfitlet:/home/jonbendtsen# upsmon -DD
Network UPS Tools upsmon 2.7.2
kill: No such process
   0.000000     UPS: apc1500@localhost (monitoring only)
   0.000166     UPS: Smart-UPS_3000@localhost (monitoring only)
   0.000257     UPS: R3000XR@localhost (monitoring only)
   0.000884     Using power down flag file /etc/killpower
   0.001629     debug level is '2'
   0.005681     Init SSL without certificate database
   0.011154     Trying to connect to UPS [apc1500@localhost]
   0.013431     Logged into UPS apc1500@localhost
   0.013955     pollups: apc1500@localhost
   0.014318     parse_status: [ALARM OL]


level 1 is not enough to see the ALARM in the output


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to