Here is the response I received from Perry White of Mirion as a result of 
issues we (Duke Energy) were having with water intrusion.


" First remember that with any water proof system, every part must be intact, 
clean and lubricated as needed to maintain that water proof seal.  

1)      Inspect the cable for cuts or holes.  A penetration through the outer 
sheath can lead to water intrusion through the connector (cables are pressure 
tested from the factory).
2)      Inspect the connector.  Ensure there is a proper o-ring installed (see 
below), the seal around the pins is intact, and the pins are straight.  Also 
ensure the compression nut to the cable is secure and sealed properly.
3)      Clean or ensure clean the threads and seal areas of the connector.  
Remove any dirty grease with alcohol.
4)      Lubricate the O-ring on the connector (See below).
5)      Ensure the pins are properly aligned prior inserting the connector into 
the detector.  The pin section of the connector is part of the seal and as such 
has very little margin or slop but will slide together easily when properly 
aligned.  Do Not Force the connection.  Once inserted, hand tighten the 
connector, push the connections together firmly and tighten again (this is a 
piston seal not a compression seal so the connectors should be pushed firmly 
together for the best seal).  Never utilize tools to tighten, this can damage 
the connector.

>From Ikelite, they recommend only their lubricant and their O-rings be 
>utilized:

Some non-Ikelite brands of lubricants have been known to cause softening and 
swelling of our o-rings. We recommend using only Ikelite silicone lubricant on 
all of our o-rings to prevent potential problems or flooding. Available as part 
number #0184.1 one 1cc tube or in #5020 package of four 1cc tubes. 

Thanks, Perry

Perry White
Mirion Technologies (MGPI), Inc.
South East US Sales Manager
Office:   770.432.2744 x194
Mobile: 404.642.8584
Email:   [email protected] 
www.mirion.com



Bill Byrum, CHP
EnRad Laboratories
Duke Energy
[email protected]
Phone 980.875.5811

-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, February 08, 2012 9:07 AM
To: [email protected]
Subject: Powernet: AMP-100 water intrusion


DC Cook is evaluating methods to prevent water intrusion into AMP-100
instruments for underwater monitoring.  Contract technicians mentioned the
use of a non-conductive gel in the o-ring area.  For those who are using
this, can you provide material type/vendor, and under what conditions it
can be used (SFP, cavity, etc)?

Elizabeth Emily
Associate Health Physicist
Cook Nuclear Plant
work:  269-465-5901 ext 2545
[email protected]



----------------------------------------------------------------
This e-mail message and all attachments transmitted with it from the
Nuclear Generation Group of American Electric Power are for the sole
use of the intended recipient(s) and may contain confidential and
privileged information.  Any unauthorized review, use, disclosure or
distribution is prohibited.  If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

-----------------------------------
Powernet - a service of the Health Physics Society Power Reactor Section

Powernet archives at http://www.mail-archive.com/[email protected]/

Reply to: [email protected]
If Questions, contact Mike Russell, CHP at [email protected]
-----------------------------------
Powernet - a service of the Health Physics Society Power Reactor Section

Powernet archives at http://www.mail-archive.com/[email protected]/

Reply to: [email protected]
If Questions, contact Mike Russell, CHP at [email protected]

Reply via email to