Excuse my second post.  I meant closed Weir gate.  Also, we keep a small number 
of unlatched EDs for those situations where we want to brief on expected dose 
rate alarms.

Linda

> On Jun 12, 2014, at 10:44 AM, "Sewell, Linda" <[email protected]> wrote:
> 
> Diablo Canyon does latch the dose rate alarm.  We changed our process after 
> our Fuel Handling Building event in 2012.  Briefly, the workers did not hear 
> their rate alarms because of all the other rad monitors alarms that sounded.  
> The workers got a fuel bundle too close to an open Weir gate and the empty 
> transfer canal.  They recognized the situation when a number of rad 
> monitoring devices went into alarm and moved the bridge back.  Because all 
> the alarms cleared the magnitude of the event was not recognized until RCA 
> logout.  The spotters ED indicated a rate alarm of approximately 2200 mR/hr.
> 
> Please take a look at our OE on this event.  It presents a compelling case 
> for latching the dose rate alarm.
> 
> Thanks,
> 
> Linda Sewell
> 
> On Jun 11, 2014, at 11:15 AM, "Baca, Michelle A" 
> <[email protected]<mailto:[email protected]>> wrote:
> 
> Good afternoon,
> 
> Salem would like to know if other plants set their electronic dosimeters to 
> latch for a dose rate alarm.  We have DMC 2000s (eventually going to 3000s), 
> and currently latch for accumulated dose only.
> 
> Thank you in advance for your time and consideration!
> 
> Michelle Baca
> PSEG Nuclear, LLC
> Radiation Protection
> W: 856.339.1049
> 
> 
> 
> ________________________________
> 
> The information contained in this e-mail, including any attachment(s), is 
> intended solely for use by the named addressee(s). If you are not the 
> intended recipient, or a person designated as responsible for delivering such 
> messages to the intended recipient, you are not authorized to disclose, copy, 
> distribute or retain this message, in whole or in part, without written 
> authorization from PSEG. This e-mail may contain proprietary, confidential or 
> privileged information. If you have received this message in error, please 
> notify the sender immediately. This notice is included in all e-mail messages 
> leaving PSEG. Thank you for your cooperation.
> 
> 
> PG&E is committed to protecting our customers' privacy. 
> To learn more, please visit http://www.pge.com/about/company/privacy/customer/
> -----------------------------------
> Powernet - a service of the Health Physics Society Power Reactor Section
> 
> Powernet archives at 
> https://urldefense.proofpoint.com/v1/url?u=http://www.mail-/&k=4%2BViHuL0UtSJBpVrYi3EdQ%3D%3D%0A&r=3EbX7tUN8ERxmm7x6QEnjg%3D%3D%0A&m=ikXn4rHmvXOWcmXy3t8tOUEPuFD6MxjRTmuw49t5l%2Fg%3D%0A&s=2f68a5b68c40f2366ed77d70fdcb411171c968edc8f70071aa627323bdd40e77
> https://urldefense.proofpoint.com/v1/url?u=http://archive.com/powernet%40hps1.org/&k=4%2BViHuL0UtSJBpVrYi3EdQ%3D%3D%0A&r=3EbX7tUN8ERxmm7x6QEnjg%3D%3D%0A&m=ikXn4rHmvXOWcmXy3t8tOUEPuFD6MxjRTmuw49t5l%2Fg%3D%0A&s=b36fe20d3d8d8a867f9079b1254641615de0c8ac3b2ab158e3c992038a86535e
> 
> Reply to: [email protected]
> If Questions, contact Mike Russell, CHP at
> [email protected]


PG&E is committed to protecting our customers' privacy. 
To learn more, please visit http://www.pge.com/about/company/privacy/customer/
-----------------------------------
Powernet - a service of the Health Physics Society Power Reactor Section

Powernet archives at http://www.mail-
archive.com/[email protected]/

Reply to: [email protected]
If Questions, contact Mike Russell, CHP at
[email protected]

Reply via email to