The XW6048 is rated at 52 amps RMS line to line between 5 seconds down
to 1 millisecond, so if your client's AC has a starting inrush surge of
104 amps at 240v, then yep, I think your biggest problem is not enough
inverter.  Sounds like just one additional inverter will be marginal;
depending upon the additional background loads you may want to consider
expanding to three total.  I think Mick Abraham is right on here, in his
earlier post.

 

Phil Undercuffler

Director, Battery-based and Off-grid

Conergy Sales & Systems, Americas

Our World Is Full of Energy

1730 Camino Carlos Rey Suite 103

Santa Fe, NM  87507

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> 

Direct | 505.216.3841

Toll Free | 888.396.6611 x4841

Fax | 505.473.3830

www.conergy.us <http://www.conergy.us/> 

________________________________

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Max
Balchowsky
Sent: Tuesday, August 19, 2008 6:45 AM
To: [EMAIL PROTECTED]; RE-wrenches
Subject: Re: [RE-wrenches] offgrid system question

 

You're right Mick, It is an XW 6048, there's only one and I really think
I'm going to find that the biggest problem is that there is not enough
inverter capacity capacity with just one unit (the scematic shows a 60
amp breaker on the output). The system is new ( installed within the
last 4 months and the batteries were new) The AC unit is 240 volt.....

 

Max Balchowsky

SEE Systems





 

_______________________________________________
List sponsored by Home Power magazine

[email protected]

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to