Jeff,
Re remote starting, we have had experience with these generators as being
two-wire and easy to control:
    -all Kohler LP from the old 6.5RMY through 20RY
    -Onan RS20000 - I understand the new units are 2-wire like Kohler. This
one was.
    -Coleman 10kW with Honda engine.
All required two wires only and no additional hardware.
Allan
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Yago
Sent: Wednesday, September 03, 2008 9:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Remote generator start


I know this subject has come up from time to time in small pieces, but would
like a collective set of answers.  As you know, some generators are very
easy to remote start from an inverter using only a simple relay and 2-wire
connection.  Make the contact and the generator starts and runs, break the
contact and it stops.  The Kohler line of generators have this start and
stop control and was easy to connect to the spare relay in the old Trace
SW40 inverter and the newer Outback inverters.
 
What generators in the 8 to 15 kW range have you found easy to remote start
from an inverter, and which models or brands were a nightmare?  
 
What other hardware or controls were required to get it to work?   
 
How many control wires were required out to the generator?
 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to