Nick:

I just finished the first phase of a large project for the state of California using a quad stack. The generators are three phase but the campus is all split phase. They were able to center tap one winding of the generators and use the two phases on either side. I was skeptical, thinking that the phase angle would be 120 degrees, not 180 degrees as required for the quad stack, but an oscilloscope proved the 180 degree phase angle. The quad stack is happy with the two phases of the three phase. Let me repeat that this is only possible because the winding on the generator between the two phases we are using was center tapped and bonded to create a neutral.

I was told that many large three phase generators have a 12 winding configuration. I belive that this configuration will allow the center tap to be made. You should verify this will not void any warranties or damage the generator.

The down side is that there is some loss of generator capacity, but it was far less than I predicted, somewhere about 80% of name plate.

I have pictures of the PV and inverters on our web site, but not of the generators. I think they are 30 KVA Kohlers. As a side note, the generator system is very unique. There are three generators and they can run one, two or three in synchronization, as needed. Also, the inverter system does not through-put power. The generator control system switches the generators off the main buss moments before switching the inverters onto the main buss. To further complicate things, the generators must be loaded at close to capacity at all times to reduce emissions. There is a load bank that switches in and out to accomplish this. It took Kohler Corporate many trips to get this working, and I'm not sure I really belive they have all of the bugs out yet.

Good Luck,

William Miller


At 09:03 PM 1/14/2009, you wrote:
Hi Nick,

Why you want the change from single to 3 phase?
Pretty big difference that.


jay

peltz power


On Jan 14, 2009, at 4:56 PM, Nick Houser wrote:

Has anybody done  (or even TRIED) this?  The Quad stack is exactly
like page 20 of the manual. Owner
refuses to let me convert the Quad panel to three phase as he won't
give up the forth inverter' contribution.
Ditto repacing or converting the generator. Related question:  If
the transformer is a viable option, how do
I size it? Help. please, I'm running out of options. Nick Houser,
Off Grid Services, Powell River, BC
[email protected]    604-483-4898  Fell free to contact me off
list, and Happy New Year. ALL!!!!!

--
Using Opera's revolutionary e-mail client: http://www.opera.com/mail/
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to