Jeff,



Why not send DC back to the garage and set your Sunny boy there.

By sending 350VDC back you will have considerably less voltage drop to deal 
with than 240 VAC.  There is no charge controller as it is AC coupled.



I know the old SW4024 takes AC both ways on the AC in.



I am doing a similar installation, AC coupled, but with outback VFX instead of 
Xantrex.

The outback will not backfeed the grid as it is an off grid inverter.  It has 
an internal transfer switch.  The Aux relay has to be connected to a relay to 
disconnect the sunny boy ac circuit to prevent of overcharging the batteries as 
there is no charge controller.  So yes the sb charges the batteries and feeds 
the subpanel both.



When the grid fails the sunny boy disconnects.  After 5 minutes it will see the 
ac from the outback battery backup and reconnect (thru the emergency panel).  
Outback has an ac coupling paper on their website.  I am not familiar with the 
new xantrex's.



Steve



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jeff Yago
Sent: Sunday, January 18, 2009 11:31 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Back feeding battery inverter with grid-tieinverter



I know this subject has come up before, but there have been several different 
suggested ways to handle the problem and I was hoping for easiest.  We install 
lots of both on grid and off grid systems.  However, we have a client that will 
require a ground mounted array much futher away from the inverter and batteries 
in the garage than we normally would want to do since the voltage drop for this 
long distance would be excessive at low voltage even with large cables.  We 
have decided to locate a weather-proof sunnyboy grid-tie inverter at the array, 
and supply 120/240 volts to the critical loads sub-panel which is supplied by a 
Xanrex XW inverter and battery bank in the garage. I realize there are several 
design issues here when the grid is down,  since we want the grid-tie inverter 
to remain on but be blocked from the grid by the Xantrex inverter.



The question is, what is the best way to keep a load on the sunnyboy since it 
will not be grid connected during an outage.  Also, is there a best way to feed 
the output from the Sunnyboy to the Xantrex that does not just power the 
sub-panel loads during an outage, but also will re-charge the battery bank 
through the Xanrex?



If you back-feed the Xanrex from the sub-panel it is normally supplying with 
output from the Sunnyboy, will the Xanrex see this input and think the grid is 
up and be able to re-charge the battery bank?



Will we need any separate transfer switches or power relays?



Thanks,



Jeff Yago



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to