The Outbacks will definitely work. We recently completed and Fronius AC coupled system (ran DC on the home run) and back feeding the Outback quad stack. We ran short on relays, so we used a Morningstar Relay Driver which was very simple to use and gave us 4 additional programmable relays. When the batteries fill up we have the first relay kick on an electric space heater, a second one kicks on some ice melters and the third cuts the power between the Fronius and the AC panel. It tested out great and I am returning to commission it this Thursday-so we shall see.
Our system is an off grid system though and I am not sure how it would work with the grid without the GFX inverters. We have the generator for back-up. Mark Dickson Oasis Montana Inc. <http://www.oasismontana.com/> <http://www.oasismontana.com/> www.oasismontana.com www.grid-tie.com <http://www.grid-tie.com/> <http://www.pvsolarpumps.com/> <http://www.pvsolarpumps.com/> www.PVsolarpumps.com _____ From: [email protected] [mailto:[email protected]] On Behalf Of Steve Johnson Sent: Tuesday, January 20, 2009 2:47 PM To: RE-wrenches Subject: Re: [RE-wrenches] Back feeding battery inverter with grid-tieinverter (This has already been said a few times but I am testing my new email on the list and might as well put in my 2 cents. the first one bounced back so I'm checking registration again) steve Jeff, Why not send DC back to the garage and set your Sunny boy there. By sending 350VDC back you will have considerably less voltage drop to deal with than 240 VAC. There is no charge controller as it is AC coupled. I know the old SW4024 takes AC both ways on the AC in. I am doing a similar installation, AC coupled, but with outback VFX instead of Xantrex. The outback will not backfeed the grid as it is an off grid inverter. It has an internal transfer switch. The Aux relay has to be connected to a relay to disconnect the sunny boy ac circuit to prevent of overcharging the batteries as there is no charge controller. So yes the sb charges the batteries and feeds the subpanel both. When the grid fails the sunny boy disconnects. After 5 minutes it will see the ac from the outback battery backup and reconnect (thru the emergency panel). Outback has an ac coupling paper on their website. I am not familiar with the new xantrex's. Steve -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeff Yago Sent: Sunday, January 18, 2009 11:31 PM To: RE-wrenches Subject: Re: [RE-wrenches] Back feeding battery inverter with grid-tieinverter I know this subject has come up before, but there have been several different suggested ways to handle the problem and I was hoping for easiest. We install lots of both on grid and off grid systems. However, we have a client that will require a ground mounted array much futher away from the inverter and batteries in the garage than we normally would want to do since the voltage drop for this long distance would be excessive at low voltage even with large cables. We have decided to locate a weather-proof sunnyboy grid-tie inverter at the array, and supply 120/240 volts to the critical loads sub-panel which is supplied by a Xanrex XW inverter and battery bank in the garage. I realize there are several design issues here when the grid is down, since we want the grid-tie inverter to remain on but be blocked from the grid by the Xantrex inverter. The question is, what is the best way to keep a load on the sunnyboy since it will not be grid connected during an outage. Also, is there a best way to feed the output from the Sunnyboy to the Xantrex that does not just power the sub-panel loads during an outage, but also will re-charge the battery bank through the Xanrex? If you back-feed the Xanrex from the sub-panel it is normally supplying with output from the Sunnyboy, will the Xanrex see this input and think the grid is up and be able to re-charge the battery bank? Will we need any separate transfer switches or power relays? Thanks, Jeff Yago
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org