Hey Chris,
Thanks for checking.
All settings are default except for charge voltage, float voltage,
absorb time, rebulk voltage, and equalize. The battery bank is 11.7
kWh, not what I would call small. We specialize in large RV charging
systems and most batteries are 440AH and larger.
Larry
On Mar 27, 2009, at 5:52 PM, Christopher Freitas wrote:
I don't know the answer but I have forwarded this question to Darren
Emmons (the FM80 software engineer) to have him reply. I am
travelling internationally right now and may not have email access
for a few days.
The auto restart mode should not need to changed - I haven't seen a
situation like you describe but I suspect its just an issue of the
setting and probably the small battery size used in this RV
application.
Christopher Freitas
OutBack Power
Christopher
----- Original Message -----
From: [email protected] <[email protected]
>
To: RE-wrenches <[email protected]>
Sent: Fri Mar 27 16:44:59 2009
Subject: [RE-wrenches] Outback FM80 problems
Wrenches,
Last week I had an FM80 that would operate in bulk mode while reducing
the current to a few amps on a 1200 watt RV system. The customer said
he had to reset the controller several times through the day. After
every reset, full amperage was delivered and the controller would
eventually transition to absorb and float. I replaced the controller
from stock and put it on the bench. It works just fine with no other
equipment attached to the battery.
My question is about the auto restart mode. Default is 0. Should Mode
0 continue to track the Vmp thru the day or must one use mode 1 and
force restarts? The MX60 had a Sweep Interval that could be programmed
for every few minutes. Has this been replaced by the Auto Restart
Mode?
Larry
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is
confidential, and may also be protected by attorney-client or other
privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you are
hereby notified that any retention, dissemination, distribution, or
copying of this communication is strictly prohibited. Please reply
to the sender that you have received the message in error, then
delete it. Thank you.
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org