Larry,

On the RV was a modified sine wave or a SW inverter installed ?

Darren Emmons
Outback Power


----- Original Message -----
From: [email protected] <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Fri Mar 27 16:44:59 2009
Subject: [RE-wrenches] Outback FM80 problems

Wrenches,

Last week I had an FM80 that would operate in bulk mode while reducing 
the current to a few amps on a 1200 watt RV system. The customer said 
he had to reset the controller several times through the day. After 
every reset, full amperage was delivered and the controller would 
eventually transition to absorb and float. I replaced the controller 
from stock and put it on the bench. It works just fine with no other 
equipment attached to the battery.

My question is about the auto restart mode. Default is 0. Should Mode 
0 continue to track the Vmp thru the day or must one use mode 1 and 
force restarts? The MX60 had a Sweep Interval that could be programmed 
for every few minutes. Has this been replaced by the Auto Restart Mode?

Larry
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to