William, In the Xantrex "XW Power System Installation Guide", pages 2-34 to 2-37, there is a parts list and some diagrams on the wiring of a 3-inverter system. The parts list calls for two 5 ft (62" hole-to-hole) 4/0 battery cables to connect the third inverter up to the Distribution Panel.
Also shown is the use of an external bypass switch to make up for the lack of enough AC breaker spaces in a single Distribution Panel. It shows a breaker/interlock panel, but a 2-pole manual transfer switch will also work. Either way, it should be rated for at least 200A. Brian Teitelbaum AEE Solar From: [email protected] [mailto:[email protected]] On Behalf Of William Miller Sent: Tuesday, April 28, 2009 8:49 PM To: RE-wrenches Subject: [RE-wrenches] 3 Xantrex XW system Friends: We are in the midst of installing our first 3 XW system. Several questions arose during our work today. I appreciate input any of you might have. 1. Did you find the leads from the Xantrex connection ki long enough for the third inverter? 2. How many AC sources did you connect? 3. Did you provide bypass capabilities? 4. How did you interlock the bypass capabilities? 5. Did you use one or two Power Distribution Panels? 6. Can you offer any advice on how best to connect this equipment? Thanks in advance. William Miller Please note new e-mail address and domain: William Miller Miller Solar Voice :805-438-5600 Fax: 805-438-4607 email: [email protected] http://millersolar.com <http://millersolar.com/>License No. C-10-773985
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org