Thanks, Mark, for answering William's question. You took the words right out of 
my mouth.

But I wonder if William can get away with a 100A transfer switch, since it is 
only a 100A service. I guess it would be up to the inspector. S/he might be 
concerned to somebody could upgrade the service at some time in the future, and 
not upgrade the transfer switch, but I would think that that would be the fault 
of the person doing the service upgrade, not William's. But as we all know, 
inspectors can be quirky.

But then there is the issue of the 82A generator output. 82A x 1.25 = 102.5A

Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Edmunds
Sent: Thursday, April 30, 2009 9:34 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 3 Xantrex XW system

Hi William - the 200A rating is to allow for the fact you may have 48A of pass 
through from the grid to the critical loads with the normal 60A breakers in the 
system.

Mark

From: [email protected] 
[mailto:[email protected]] On Behalf Of William Miller
Sent: Thursday, April 30, 2009 8:35 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 3 Xantrex XW system

Brian:


One more question:  Why must the external transfer be "rated for at least 200 
amp?"  The utility feed is 100 amp, the generator is 82 amp and if my 
arithmetic is correct, the inverters can generate 75 amps.

William



At 10:00 PM 4/28/2009, you wrote:


William,

In the Xantrex "XW Power System Installation Guide", pages 2-34 to 2-37, there 
is a parts list and some diagrams on the wiring of a 3-inverter system. The 
parts list calls for two 5 ft (62" hole-to-hole) 4/0 battery cables to connect 
the third inverter up to the Distribution Panel.

Also shown is the use of an external bypass switch to make up for the lack of 
enough AC breaker spaces in a single Distribution Panel. It shows a 
breaker/interlock panel, but a 2-pole manual transfer switch will also work. 
Either way, it should be rated for at least 200A.

Brian Teitelbaum
AEE Solar

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to