if you read 690.64b it does mention both the buss rating AND conductors.

for years and years I thought it was just for the buss rating until i got 
called recently for the feeders being undersized and unable to accommodate the 
solar within 120%. I see a lot of sentiments in this thread that it is only for 
busing, and I would really like to discover a reference to that. Someone told 
me something about the difference of having main lugs and main breakers in the 
sub panel... i am looking into it.

>From the literal of 690.64 it would seem that if you are fed with #4 than you 
>are stuck with 120% of 100a regardless of the sub panel rating.

nick



      