Dick:

Your logic is correct but incomplete. Consider it like this: The buss bars in the service panel can handle 100 amps (they are rated for that amount). The main breaker feeds 100 amps into that buss, maximizing it's capabilities. If you feed an additional 40 amps into that buss bar, you have the potential of exceeding the ampacity of that buss assembly. If no other loads are fed from that buss bar, there is no over current scenarios. Say, however, someone puts more breakers on that buss bar and draws 140 amps from them. 100 amps comes in from the utility, 40 amps comes in from the PV and the buss is overloaded.

This is the scenario for which 690.64(B) was written. This will occur only if the overload amperage is not drawn from a space on the buss bar between the utility feeder and the PV feeder. If, however, the PV feeder breaker and the utility feeder are both on one end of the buss and the load is on the other end, then the loads are additive on the buss assembly.

Some want the code passage re-written to say that if the feeder is on one end of the bus assembly and the PV is on the other, there is no possibility of an overdraw on the buss bar and the installation is legal. This has not happened yet.

William




At 03:47 PM 8/1/2009, you wrote:
William,

I don't know if I've solved Brian's dilemma yet either. But, with regard to your
example below, if the 100 amp meter main is accepting 20 amps, or even all of
the 50 amps of PV, that would mean that the house, at that moment, presented no
load at all, and that all the PV would be backfeeding the grid, turning the
meter backwards. That, of course, would mean the main 100 amp breaker is only
handling 50 amps, well below its rating. Likewise the feeder from the house
would only be carrying the 50 amps from the PV, instead of anything near it's100
amp rating. The code can be perverse, but it's my understanding that the point
of 690.64(B) is to ensure none of the distribution components are exposed to
overcurrent, not to arbitrarily throw numbers around.

I was just kidding about offering you those 200 amp Milbank breakers. I've got
to figure out how to list them on Ebay.

Dick

--- You wrote:
Dick:

I don't believe you have solved Brian's dilemma yet.  It is my
understanding that if one is going to install a load side tape, the back
feed calculations need to work for every link of the distribution system
upstream to the meter.  In the scenario you suggest, that will not be the
case.  The 100 amp meter main on Brian's project will still  accept only 20
amps of PV AC feed, still not satisfying his requirements.
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.392 / Virus Database: 270.13.39/2275 - Release Date: 08/01/09 09:38:00

Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600     Fax: 805-438-4607
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to