Orion,

If the Generac generator is running at 58Hz, it means that the engine speed is 
about 120rpm too low (on a 3600rpm genny; half that for a 1800rpm unit). There 
should be some sort of adjustment to the engine governor on the unit, but I'm 
not familiar enough with the newer Generacs to know where it is, or even if 
there is an adjustment. If it's electronically governed, rather than 
mechanically, you may need to replace the electronic unit.

Or, you may just be overloading the generator. You might try turning down the 
charge rate on the OutBacks.

All this is still not a  guarantee that the OutBacks will sync up.


Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of Orion Thornton
Sent: Monday, September 28, 2009 11:43 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Battery Charger

Wrenches,

We recently installed a grid-tie battery backup system using two Outback GVFX 
3648 inverters.  The client has an existing Generac backup generator, 8 kW @ 
240VAC.  From the beginning we told the client that the power quality from the 
Generac may not be within tolerance to integrate with the grid-tie inverters 
and charge batteries.  This assumption was confirmed today when we commissioned 
and tested the system.  The output frequency of the Generac was 58 hz.

To get to the point does anyone have a battery charger they recommend for this 
application?-8 kW @ 240VAC generator output to 48VDC battery bank.  Or maybe 
another suggestion to be able to integrate the generator into the system, we 
are also planning on manually transferring the generator output to power the 
critical loads if an inverter goes down.

It also seems that the dc genset controls through the mate would be the best 
way to control the battery charger-any thoughts?

Thanks in advance for any input.

Orion Thornton
Project Manager
Independent Power Systems
NABCEP Certified PV Installer
(W) 406.587.5295
(C)  406.249.9912
www.solarips.com<http://www.solarips.com/>




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org