There is an existing automatic transfer switch—isolating the grid and feeding 
in the generator.

 

Orion 

 

 

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, September 28, 2009 6:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Charger

 

I am curious how you connect a generator to the GVFX? It only has one AC input 
that us used for the grid.

Todd

On Monday, September 28, 2009 11:43am, "Orion Thornton" 
<[email protected]> said:

Wrenches,  

 

We recently installed a grid-tie battery backup system using two Outback GVFX 
3648 inverters.  The client has an existing Generac backup generator, 8 kW @ 
240VAC.  From the beginning we told the client that the power quality from the 
Generac may not be within tolerance to integrate with the grid-tie inverters 
and charge batteries.  This assumption was confirmed today when we commissioned 
and tested the system.  The output frequency of the Generac was 58 hz.

 

To get to the point does anyone have a battery charger they recommend for this 
application?—8 kW @ 240VAC generator output to 48VDC battery bank.  Or maybe 
another suggestion to be able to integrate the generator into the system, we 
are also planning on manually transferring the generator output to power the 
critical loads if an inverter goes down.

 

It also seems that the dc genset controls through the mate would be the best 
way to control the battery charger—any thoughts?

 

Thanks in advance for any input.

 

Orion Thornton

Project Manager

Independent Power Systems

NABCEP Certified PV Installer

(W) 406.587.5295

(C)  406.249.9912

www.solarips.com <http://www.solarips.com/> 

 

 

 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to