A "Low AC Volts" error is very typical for a cave in battery voltage under load. I've reported in this forum before the propensity of Outback inverters to misreport error conditions.

4 L-16s is a very small battery bank. I would not be at all surprised if this was indeed a battery or related wiring problem.

William Miller





At 05:18 PM 10/1/2009, you wrote:
Content-Type: multipart/related;
        boundary="----=_NextPart_000_016B_01CA42E1.ED2C51E0"
Content-Language: en-us

Tom,

The L-16's are 6v. So, they all had to be in series to operate at 24v (FX2024 is a 24v inverter).
Dave

From: [email protected] [mailto:[email protected]] On Behalf Of The Office of Tom Duffy
Sent: Thursday, October 01, 2009 8:53 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] FX2000 / Trojan battery question

Bob
On the other note: Were the L-16s in series or series/parallel? Also were the voltage readings and Hydrometer readings done on an active bank or "at rest" and what were the readings?

  Tom Duffy
  Systems Design Engineer
4ce320d.jpg

     <mailto:[email protected]>[email protected]
       575-539-2111 X 301

----------
From: [email protected] [mailto:[email protected]] On Behalf Of robert ellison
Sent: Thursday, October 01, 2009 5:40 PM
To: RE-wrenches
Subject: [RE-wrenches] FX2000 / Trojan battery question

Just visited a site with a 04 version FX2024 The inverter is shutting down and showing "low AC output voltage" It is hooked to 4 Trojan L-16 G batteries. When i arrived the voltage was 23.8, the other day when i arrived it was 25.5 volts and shut down both times with the same error showing. There are 1050 watts of panels and an MX 60 on the battery bank also. In the past when the batteries went low it would show a low battery error, so i don't expect that is the problem. Loads are minimal
Disconnecting the battery or starting the generator clears the error.

When i called Outback i was told there was a $250.00 "out of warranty charge" as well as a retail of $1400 for the boards. She also insists it was probably a bad battery bank, or at least needing an eq charge. It just had one 9 days ago. The hydrometer readings are all close and the voltages similar.

Anyone run into this before and have any knowledge on this error?

On another note, has anyone had any Trojan L-16 G batteries with cell failures? The date code is J8 I have had 2 in the last year, one was under warranty and the last one out of warranty.
Anyone else had this problem or am i just unlucky?

Thanks,
Bob

<<attachment: 4ce320d.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to